Question 9

During work on a temporary outdoor structure, a steel support pole touches a damaged cable connected to the UK mains. The supply is switched on, and a worker is holding the pole. The worker's body resistance is the same in all three situations.

SituationConductor touching the poleResistance of the path between the worker's boots and earth
Plivelow
Qlivehigh
Rneutrallow

A supervisor says that P and Q would give the same risk of a large current through the worker because both involve the live conductor. Another supervisor says that R would give the same risk as P because both have a low-resistance path to earth. Evaluate these claims and identify which situation gives the greatest risk of a large current through the worker.

[4]
Markscheme
  1. GCSE
  2. /Physics
  3. /2.3 Domestic uses and safety

95 exam-style questions on AQA GCSE Physics 2.3 Domestic uses and safety, covering 2.3.1 Direct and alternating potential difference and 2.3.2 Mains electricity. Each one has a worked solution and a mark scheme showing where the marks go.