Question 30

A step-down transformer supplies workshop equipment at a railway maintenance depot. Its primary coil is connected to a 6600 V alternating supply. The secondary coil provides 400 V and carries a current of 165 A. The transformer is 100% efficient.

An ammeter is connected in series with the primary coil.

Calculate the reading expected on the ammeter.

Use the equation

VP×IP=VS×ISV_P \times I_P = V_S \times I_SVP​×IP​=VS​×IS​

[3]
Markscheme

13.2 Transformers and the National Grid Questions

  1. GCSE
  2. /Physics
  3. /13.2 Transformers and the National Grid

108 exam-style questions on Edexcel GCSE Physics 13.2 Transformers and the National Grid, covering 13.2.1 Transformers and induction, 13.2.2 The transformer turns-ratio equation, 13.2.3 The National Grid, 13.2.4 The transformer power equation, and 13.2.5 Advantages of high-voltage transmission. Each one has a worked solution and a mark scheme showing where the marks go.