In a transformer used for a low-voltage chime system:

  • the primary voltage is 240 V
  • the primary current is 0.030 A
  • the secondary voltage is 12.0 V

Calculate the secondary current. Use the equation:

Is=Vp×IpVs I_s = \frac{V_p \times I_p}{V_s} Is​=Vs​Vp​×Ip​​
[2]
Markscheme

13.2 Transformers and the National Grid Questions

  1. GCSE
  2. /Physics
  3. /13.2 Transformers and the National Grid

28 exam-style questions on Edexcel GCSE Physics 13.2 Transformers and the National Grid. Each one has a worked solution and a mark scheme showing where the marks go.